I have a class 320 meter mounted outside on a post. 4/0 copper Service entrance conductors from meter to a J-box in the single family dwelling where they are tapped to a 100 amp disconnect and a 200 amp disconnect. Taps are sized to 310.15(B)(6), the 4/0 is sized for the load per NEC 230.90(A) ex 3. I am wondering if I need any sort of identification plate for the following two possible reasons:
1) I have two disconnects. I know in say a duplex where the discos are not grouped, each one needs a plate indicating where the other discos in the structure are, but since mine are about 4 feet apart would this not apply?
2) WAC 296-46B-230-042 (This one is for any washington state people):
"If the service conductors have a lesser ampacity than the overcurrent protection or the equipment rating that they terminate in or on, an identification plate showing the ampacity of the conductors must be installed on the service equipment"
Does this apply in my situation? The ampacity of my service entrance conductors prior to the taps is greater than either individual breaker but less than the combined rating
Thanks in advance!
1) I have two disconnects. I know in say a duplex where the discos are not grouped, each one needs a plate indicating where the other discos in the structure are, but since mine are about 4 feet apart would this not apply?
2) WAC 296-46B-230-042 (This one is for any washington state people):
"If the service conductors have a lesser ampacity than the overcurrent protection or the equipment rating that they terminate in or on, an identification plate showing the ampacity of the conductors must be installed on the service equipment"
Does this apply in my situation? The ampacity of my service entrance conductors prior to the taps is greater than either individual breaker but less than the combined rating
Thanks in advance!