I suppose it would depend on the project delivery type. If this is a design-bid-build project, then all prospective bidders should be able to base their prices on the same design information. In that case, I would give the branch circuit sizes. If this is a design-build project, then I think you can leave much of that detail to the design arm of the design/build team.
Our standard practice is to state that all 20 amp branch circuits use #12 wire unless shown otherwise. We also include a generic clause to upsize to #10 for 120 volt, 20 amp circuits over 100 feet long. The distance is 200 feet for 20 amp 208 or 277 volt circuits.
For anything that needs a 30 amp or higher branch circuit, we include an electrical connections schedule. It lists everything that appears on the mechanical or plumbing schedule as needing a power source (e.g., supply fans, booster pumps, circulating water pumps, etc.). We show the same HP as they show, and our Excel file calculates the appropriate branch circuit design (i.e., conduit, breaker, and wire sizes). We don't show that information on the floor plans. We only show the component's name (e.g., "CP-1"), and leave it to the contractor to look for that component on the electrical connections schedule.