- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
If a solar water heater, with copper water lines running through it, is installed on the roof of the house and a short section of copper enters the attic then connects to pecs (plastic pipe) , then do I need to bond the copper.
Art. 250.4(4) says electrically conductive material likely to be energized-- I don't think this is likely to be energized. However 250.104 (A)(1) seems to suggest otherwise. Can you help this old man???
Art. 250.4(4) says electrically conductive material likely to be energized-- I don't think this is likely to be energized. However 250.104 (A)(1) seems to suggest otherwise. Can you help this old man???