230.52(A)(3) Concrete-Encased Electrode. A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(1) One or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (½ in.) in diameter, installed in one continuous 6.0 m (20 ft) length, or if in multiple pieces connected together by the usual steel tie wires, exothermic welding, welding, or other effective means to create a 6.0 m (20 ft) or greater length; or
(2) Bare copper conductor not smaller than 4 AWG Metallic components shall be encased by at least 50 mm (2 in.) of concrete and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth or within vertical foundations or structural components or members that are in direct contact with the earth.
If multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the
grounding electrode system.
Informational Note: Concrete installed with insulation, vapor barriers, films or similar items separating the concrete from the
earth is not considered to be in “direct contact” with the earth.