M makalroy Member Feb 22, 2010 #1 Hello, I just received 20 new panels for a job, and they don't have bottems. does the NEC require a bottom in MDP's or SDP's. Thanks
Hello, I just received 20 new panels for a job, and they don't have bottems. does the NEC require a bottom in MDP's or SDP's. Thanks
iwire Moderator Staff member Location Massachusetts Feb 22, 2010 #2 Wall mounted panels or floor standing switchgear?
480sparky Senior Member Location Iowegia Feb 22, 2010 #4 makalroy said: Floor standing Click to expand... Then the answer is 'no'.
tkb Senior Member Location MA Feb 22, 2010 #5 makalroy said: Floor standing Click to expand... If you didn't specify them with bottoms, they won't come with them. Standard is open bottom for floor standing units.
makalroy said: Floor standing Click to expand... If you didn't specify them with bottoms, they won't come with them. Standard is open bottom for floor standing units.
iwire Moderator Staff member Location Massachusetts Feb 22, 2010 #6 makalroy said: Floor standing Click to expand... Then that could be OK depending on what the floor is made of. If it is non-combustible you will be fine, if it is combustible you have an issue.
makalroy said: Floor standing Click to expand... Then that could be OK depending on what the floor is made of. If it is non-combustible you will be fine, if it is combustible you have an issue.