zappy said:I was just wondering.Thanks.:smile:
zappy said:I was just wondering.Thanks.:smile:
frizbeedog said:For rigid steel. RMC
Not for EMT, since you can't bury that stuff.
But you knew that already.....right?![]()
NEC 2008 said:358.10 Uses Permitted.
(A) Exposed and Concealed. The use of EMT shall be permitted for both exposed and concealed work.
(B) Corrosion Protection. Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.
However the UL White Book says that additional corrosion protection is almost always required for buried EMT or EMT installed in below grade slabs.(B) Corrosion Protection. Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.
jrannis said:You positive?