Yes. UL standards changed perhaps 15 years ago to make less subject to EM radiation like from walkie talkies, and few other issues. The latest GFCIs self test and have an indicator light that turns on or off if the GFCI quits working
For the recpt types the original versions have a circuit board that absorbed moisture.
And I suspect mfg is better today, more automated mfg and less hand assembly.
But as AC/DC pointed out if a GFCI trips its doing its job
Leviton used to make a GFCI tester that had a dial for various amounts of fault current. If you dialed in 2 mA and it tripped you had 3-4 mA of leakage somewhere. I quit using it as all the GFCIs I had in pump stations and well houses never tripped. I once had some WP glass globe lights mounted on a vault ceiling, they filled up with water but the GFCI never tripped,(all PVC no leakage to ground).
The one GFCI I had that nuisance tripped was on small 1/8 hp submersible pump someone had spliced the cable and the casing filled with water, it was a dead short. But it was a "bad GFCI".
And please remember the only way to test a GFCI is its button. The plug in testers are not the mfg recommended method