Hi all,
Any help will be greatly appreciated! Here is the scenario:
We interconnected our solar system through a supply side connection made at the utility service entrance conductors of a 1200A MSP with 1200 MCB. The conductor run from the fused PV system AC disconnect(OCPD) to the point of interconnection is 14' so we plan to use the cable limiters per the Exception of 705.31 to work around the 10' rule. However, the inspector is saying we need to comply with the 25' tap rule per 240.21(B)(2) which will result in increasing our conductor size to not less than 1/3 of the rating of MCB. In my understanding, 240.21 is for the tap conductors that receive their supply, not for conductors that backfeed the utility. Also, I believe supply side connection has the different definition to "tap" so 240.21 does not really apply to the supply side connection for solar photovoltaic. Am I right? Has anyone encountered this situation during the inspection?
Thanks!
Thanks!