UL did an investigation on hammer and staple damage to NM cable that indicates that the arc from that type of damage is too short and has too little energy to start a fire. The arc self extinguishes at about 1/2 cycle....The AFCI has to see at least 8 half cycles before it will trip.
Influence of Damage and Degradation on Breakdown Voltage of NM Cables
From the executive summary:
It seams this is just one more thing that they told us the AFCI was designed to protect against, but we now find out that this type of damage does not result in fires.
Influence of Damage and Degradation on Breakdown Voltage of NM Cables
From the executive summary:
The test results indicate that the probability of sustained arcing and ignition is low for hammer-damaged NM cable. The results also show that though a carbonized path may eventually be formed, this path formation did not lead to subsequent ignition of the cable jacket or surrounding materials, and self-extinguished after a short period of arcing.
It seams this is just one more thing that they told us the AFCI was designed to protect against, but we now find out that this type of damage does not result in fires.