In trying to meet the requirements for motor disconnect in sight of motor, would you consider a VFD to be a controller?
In our installation, the 480V VFD is in site of the motor. The VFD is fed from a breaker in another location. This is a regular molded case breaker.
After reading and re-reading 430.103, it does not seem to meet the intent.
- The disconnecting means is not in site of the controller.
- It is not over 600V
- The breaker serving the VFD is a regular molded case breaker (i.e. it does not have a permanent lockable means).
Again, if the VFD is not a controller and only a disconnect, then this would be a moot point. But I interpret the VFD to be a controller.
Any thoughts?