300.3(b)
(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment-grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4)
If there is a dead-end switch box with one single pole switch in it, run in EMT - do you guys run a neutral down to the box along with the current carrying ungrounded?
(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment-grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4)
If there is a dead-end switch box with one single pole switch in it, run in EMT - do you guys run a neutral down to the box along with the current carrying ungrounded?