While inspecting a dock using a clamp method as shown by James Shafer in
http://www.icomia.com/library/ICOMIA_File_Download.asp?BK_ID=251
or
http://www.halifaxharbor.net/Marina Grounding 6 04.pdf
I get a reading of .501 amps clamping the feed to the dock, which includes 2 undgrounded conductors, one grounded (neutral) and a grounding conductor while operating a 1500 watt hairdryer in one outlet.
This is a new commerical 14 slip dock with no shore powers, just outlets and lights, and no load at the time of the test. It has one lighting circuit and two separate outlet circuitis.
This dock is bonded to ground.
see link for detail wiring information: http://www.ameren.com/LakeOzarks/ADC_DockElectrInstal.asp
NEC 2005 with AHJ changes as listed online.I shut off the load and reading remains, fluctuating between .359 and .501.
I throw the mains feeding the dock and the current readings remain.
I had a similiar dock recently showed .10 amps but when the power was turned off, the reading left.
All outlets on both docks checked correctly for polarity and grounding.
My guess and that is what it is a guess, is that I am seeing a reading because by bonding the dock to the service and requiring a grounding electrode at the seawall the amp reading is coming from the service wiring. Whether it is stray voltage or just a better grounding system I don't know.
My question: Does this present a danger?
In the case of the commerical dock it is a 4 wire subpanel.
In the .10 amp case it is a 3 wire circuit with GFCI protection from an older house that is probably has the neutrals and grounds on a common bus.
Any insight with answers or additional test I can perform to ensure the safety of the dock owners and their guests would be appreciated.
http://www.icomia.com/library/ICOMIA_File_Download.asp?BK_ID=251
or
http://www.halifaxharbor.net/Marina Grounding 6 04.pdf
I get a reading of .501 amps clamping the feed to the dock, which includes 2 undgrounded conductors, one grounded (neutral) and a grounding conductor while operating a 1500 watt hairdryer in one outlet.
This is a new commerical 14 slip dock with no shore powers, just outlets and lights, and no load at the time of the test. It has one lighting circuit and two separate outlet circuitis.
This dock is bonded to ground.
see link for detail wiring information: http://www.ameren.com/LakeOzarks/ADC_DockElectrInstal.asp
NEC 2005 with AHJ changes as listed online.I shut off the load and reading remains, fluctuating between .359 and .501.
I throw the mains feeding the dock and the current readings remain.
I had a similiar dock recently showed .10 amps but when the power was turned off, the reading left.
All outlets on both docks checked correctly for polarity and grounding.
My guess and that is what it is a guess, is that I am seeing a reading because by bonding the dock to the service and requiring a grounding electrode at the seawall the amp reading is coming from the service wiring. Whether it is stray voltage or just a better grounding system I don't know.
My question: Does this present a danger?
In the case of the commerical dock it is a 4 wire subpanel.
In the .10 amp case it is a 3 wire circuit with GFCI protection from an older house that is probably has the neutrals and grounds on a common bus.
Any insight with answers or additional test I can perform to ensure the safety of the dock owners and their guests would be appreciated.