billydrowne
Member
- Location
- Massachusetts
- Occupation
- electrician
Company I work for recently installed a power pedestal on a floating dock. 100ma GFI protection for the whole circuit out of a specifically made marine disconnect, submersion rated marine cable, individual GFI protection at all receptacles and equipment at the pedestal. Supposedly a diver was re connecting a set of chains to mooring blocks underwater to keep the docks in place and got shocked WHILE submerged. Everything is on a lake that feeds other ponds, canals, etc, we really have no way to bond the water around everything being that its so large and not man made. Took voltage readings at the pedestal to the water, 120v from each phase to the water, neutral and ground was showing 4v to the water. Another section of dock has an aluminum ladder in the water, go from ladder to water and get 1-3vdc. Our best guess is that one of their boats, or a neighboring boat or dock may be leaking current into the water and our system is not picking anything up. Called our local inspector and he re assured us our equipment would have picked anything up if it was a problem on our install. our solution is to install some from of an equipotential plane to all metallic parts much like a swimming pool. Any thoughts on this one would be highly appreciated.