marcerrin

Senior Member
Residential dock. 50 amp feeder to a "lighthouse" pedastal on the dock. Pedastal has 50 amp breaker that feeds an integral TL receptacle, and a 20 amp breaker that feeds an integral 120v GFCI recep. Question is; do you need a disconnect at the shore.
I have a lock-out on the OCPD in the house. The pedastal sits on the dock, about 20' from shore.
I've looked in the NEC and can't find a code reference.

*remember, this is a dock for use at a private residence.
 
Residential dock. 50 amp feeder to a "lighthouse" pedastal on the dock. Pedastal has 50 amp breaker that feeds an integral TL receptacle, and a 20 amp breaker that feeds an integral 120v GFCI recep. Question is; do you need a disconnect at the shore.
I have a lock-out on the OCPD in the house. The pedastal sits on the dock, about 20' from shore.
I've looked in the NEC and can't find a code reference.

*remember, this is a dock for use at a private residence.

Check out 682
 
not sure what has changed since 05

Not a lot.

This


682.13 Wiring Methods and Installation.
Liquidtight flexible metal conduit or liquidtight flexible nonmetallic conduit with approved fittings shall be permitted for feeders and where flexible connections are required for services. Extra-hard usage portable power cable listed for both wet locations and sunlight resistance shall be permitted for a feeder or a branch circuit where flexibility is required. Other wiring methods suitable for the location shall be permitted to be installed where flexibility is not required. Temporary wiring in accordance with 590.4 shall be permitted.
This

III. Grounding and Bonding
682.30 Grounding.
Wiring and equipment within the scope of this article shall be grounded as specified in Part III of 553, 555.15, and with the requirements in Part III of this article.
And

682.31(B) Feeders. Where a feeder supplies a remote panelboard, an insulated equipment grounding conductor shall extend from a grounding terminal in the service to a grounding terminal and busbar in the remote panelboard.
 
Marcerin,
I'm sure you are being careful. Or you woudn't be asking questions. I just thought this article might be an intersesting read. Since it is about an electrocution at a dock. It was due to stray current in the water.

http://www.mikeholt.com/newsletters.php?action=display&letterID69

It says the letter no longer exist. I'll try to find it.
It's titled ." The electric shock drowning of Samantha Chipley"
It's in the newsletter section of this site.
 
Last edited:
I think 555 is the article that you should be looking at and there is no requirement , that I see ,..for a disconnect other than the one called for in article 555.17

Whoops just read the scope for 555.. " single family dwelling are not covered by this article......
 
Last edited: