doctors office exam room in slab roughin

Status
Not open for further replies.

bcarol67

Member
i failed an inspection for exan rm. in slab rough I used pvc boxes and pipe. the inspector says only metal boxes and rigid is allowed in exam rooms. I cannot find it in the code book. Please help.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Welcome to the forum. Your answer is 517.13(A) He is wrong about only RMC being allowed though.

Roger
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Take a look at 517.13

(sorry Roger. I had to look it up..you probably did it from memory :) )

but at least we agreed
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Gus, we are on the same page.
icon14.gif


Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
thank you for your help but look at 517-13b methods

517.13(B) (BTW what year NEC are you using?) is in addition to 517.13(A), it doesn't relieve the requirements of 517.13(A)

517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).

Roger
 

bcarol67

Member
exam rm.

exam rm.

i wasnt there to meet the inspector but thanks for all the help. looks like ill be replacing the pvc.
 