May i ask why "no"?
Would that mean room with one entrance + one working space is fine even-though the Busway rating is more than 1200a?
NotedDouble checking that you realize that 110.33(A)(1) is for >1000V.
Even-though there is a plug-in with a terminated feeder?110.33(A)(1) is for switchgear and control panels. Busway is neither of those.
Completely different UL Standard, so no, busway is not switchgear or a control panelNoted
Even-though there is a plug-in with a terminated feeder?