I have read through the NEC and I can't find a specific reference that says I have to have and equipment grounding conductor supplied to a device that uses 24VDC. Two things I am currently up against:
A control panel which has a 480 to 24VDC power source in it supplies 5 sub panels. The source is limited to 1000VA and the conductors used to feed the remote panels are Two #6's for DC+ and Two #6's for DC-. My question here is do I have to supply a grounding conductor to the sub panels? And second question: IF the sub panels feed individual devices used for controls (level probes, actuators, etc) do I have to provide and equipment grounding conductor to the devices themselves? The level probes are in metal housings. If you could please provide code references with any explanation I would appreciate it. My dilemma stems from the fact that currently the DC source has the DC- side connected to the ground bus in the cabinet it is supplied from. The sub panels have #14 Grounding wired instelled and connected to the eclosure. I am being told the #14 has to be replaced with two #6's per 250.122(B). I am reading article 250 part VIII in the 2014 NEC, and I am having a hard time deciding if any of the equipment (SUB panels, or devices fed from sub panels) are actually required to be grounded? Thanks in advance
A control panel which has a 480 to 24VDC power source in it supplies 5 sub panels. The source is limited to 1000VA and the conductors used to feed the remote panels are Two #6's for DC+ and Two #6's for DC-. My question here is do I have to supply a grounding conductor to the sub panels? And second question: IF the sub panels feed individual devices used for controls (level probes, actuators, etc) do I have to provide and equipment grounding conductor to the devices themselves? The level probes are in metal housings. If you could please provide code references with any explanation I would appreciate it. My dilemma stems from the fact that currently the DC source has the DC- side connected to the ground bus in the cabinet it is supplied from. The sub panels have #14 Grounding wired instelled and connected to the eclosure. I am being told the #14 has to be replaced with two #6's per 250.122(B). I am reading article 250 part VIII in the 2014 NEC, and I am having a hard time deciding if any of the equipment (SUB panels, or devices fed from sub panels) are actually required to be grounded? Thanks in advance