250.122(F)(1)(b) requires us to up-size the equipment grounding conductor for parallel feeders, but only when the equipment grounding conductor is a wire-type. If the equipment grounding conductor is RGC, IMC or EMT, no upsizing is required.
So, if we run no ground wire at all, we have adequate grounding, but when we run a ground wire, it needs to be a bigger than the ground wire that would otherwise be more than adequate.
And how about 250.122(F)(2)? Under some circumstances, the jacket of AC and MC cable is permitted to be the grounding conductor. If a cable is listed according to 250.118(8) or (10)(b), does the grounding conductor inside have to be upsized for paralleling?
So, if we run no ground wire at all, we have adequate grounding, but when we run a ground wire, it needs to be a bigger than the ground wire that would otherwise be more than adequate.
And how about 250.122(F)(2)? Under some circumstances, the jacket of AC and MC cable is permitted to be the grounding conductor. If a cable is listed according to 250.118(8) or (10)(b), does the grounding conductor inside have to be upsized for paralleling?