I was asked to install a ceiling fan in a 2nd floor apartment.
It is a older building and power is plumbed though the light boxes.
The Existing 4" octagon box has 5 1/2" conduits entering the box 4 on top one on the side.
All the wire was old type R and removed. THHN will be pulled in to add some modern required circuits and AFCI.
Now the box is quite central.
Box fill all #12 conductors:
Conduit A 6 conductors
Conduit B 2 conductors spliced
Conduit C 5 conductors spliced
Conduit D 3 conductors spliced
_____________________________________
16 Volumes * 2.25 = 36 CUIN
Add 20% for future expansion (as per specs) = 43.2
(EMT is the ECG)
I did find a $20 or so Raco 284 Gorilla ring but this is wood construction and the box seems like it is for a poured floor assembly, and I dont now if the 4 shepherds hook 90's will push up that far to accomidate the box.
http://www.hubbell-raco.com/images/catalog/pdfs/A09-A26.pdf
I can get out of the 20% for future expansion if needed but I am still at a loss for a 36 CUIN fan support box.
I could use a standard 4-11/16 box and 3/0 mud ring and support the fan off a 2X4 however the wording of 314.27(C) has changed to seemingly require that the box be solely capable of supporting the fan?
Thoughts?
It is a older building and power is plumbed though the light boxes.
The Existing 4" octagon box has 5 1/2" conduits entering the box 4 on top one on the side.
All the wire was old type R and removed. THHN will be pulled in to add some modern required circuits and AFCI.
Now the box is quite central.
Box fill all #12 conductors:
Conduit A 6 conductors
Conduit B 2 conductors spliced
Conduit C 5 conductors spliced
Conduit D 3 conductors spliced
_____________________________________
16 Volumes * 2.25 = 36 CUIN
Add 20% for future expansion (as per specs) = 43.2
(EMT is the ECG)
I did find a $20 or so Raco 284 Gorilla ring but this is wood construction and the box seems like it is for a poured floor assembly, and I dont now if the 4 shepherds hook 90's will push up that far to accomidate the box.
http://www.hubbell-raco.com/images/catalog/pdfs/A09-A26.pdf
I can get out of the 20% for future expansion if needed but I am still at a loss for a 36 CUIN fan support box.
I could use a standard 4-11/16 box and 3/0 mud ring and support the fan off a 2X4 however the wording of 314.27(C) has changed to seemingly require that the box be solely capable of supporting the fan?
Thoughts?