Good afternoon gentleman.
I have a question that occurred on job site.
We have Murray 8 meter stack on a box under it with 4 live exposed terminals.
Is that box officially an auxiliary gutter or is the whole assembly a manufacturers product?
Everything is supplied by Murray.
Is it up to 2008 nec or not?
thank you
376.56 (4)
(4) Live Parts. Power distribution blocks shall not have uninsulated live parts exposed within a wireway, whether or not the wireway cover is installed.
http://w3.usa.siemens.com/powerdist...t-catalog/Documents/sf-11-sect-03-034-038.pdf