Its sure looks like it to me, unless you use a 50 amp setup. I do not see how you could use a 20 or 30 amp generator inlet box with a generator made after 1-1-2011. Am I missing something?
Does this article in EC mag help?
Wouldn't it depend on whether the grounding conductor is bonded to the generator neutral? As long as the generator neutral floats, I would think it would be OK with solid neutral switches. The house neutral-ground bond isn't causing any grief if the generator neutral is floated.
Only if there is a return path, back to the generator's grounding point, that is not through the GFCI.I don't think so. The generator has a GFCI. A home electrical system has the ground and grounding conductors bonded together. A gfci will trip if the two are together.
I don't think so. The generator has a GFCI. A home electrical system has the ground and grounding conductors bonded together. A gfci will trip if the two are together.
That would also require the neutral bond of the house to be on the line side of the transfer switch, not in the panel, making the house panel a sub-panel, which would require a service-rated T/S or separate main disco.The only way for it to work would be to use a 3 pole transfer switch and transfer the neutral. but the neutral to ground bond will have to remain at the generator.
That would also require the neutral bond of the house to be on the line side of the transfer switch, not in the panel, making the house panel a sub-panel, which would require a service-rated T/S or separate main disco.
If I'm not mistaken, that is.
That would also require the neutral bond of the house to be on the line side of the transfer switch, not in the panel, making the house panel a sub-panel, which would require a service-rated T/S or separate main disco.
If I'm not mistaken, that is.
Only if there is a return path, back to the generator's grounding point, that is not through the GFCI.
As suemarkp said, if the generator is 'floating' there is no complete circuit during normal operation.
Many portable generators do not bond the neutral. The GFCI will work if there is some type of current path that is other than the two conductors that feed the GFCI. In general that would take more than one fault. There is no easy way to tell what generators bond the neutral and what ones don't unless you look in the manual. Even with in the same brand they do it both ways.