BoilerBB
- United States
- Engineer
I am trying to verify that a small to mid-size piece of industrial equipment is in NEC compliance while making wiring changes to meet the installation requirements for a UL listed component. The safety disconnect switch box used on the piece of equipment is only UL listed for 14 AWG wire and larger. The equipment is wired with all 16 AWG wire into the switch box. NEC section 312.8 Switch and Overcurrent Device Enclosures Section A reads as follows:
“(A) Splices, Taps, and Feed-Through Conductors
The wiring space of enclosures for switches or overcurrent devices shall be permitted for conductors feeding through, spliced, or tapping off to other enclosures, switches, or overcurrent devices where all of the following conditions are met:
This section implies that wire splices would be allowed inside the switch box as long as the total area of the splices and conductors don’t exceed 75% of the cross-sectional area.
Although it is not ideal, my solution is to use splice connectors (specifically WAGO 221 Series Lever Nuts) to splice together 14 AWG wires from the load terminals of the switch box to the 16 AWG wires that power the equipment inside the switch box. I have included sample pictures for reference.
I have checked with the switch box manufacturer that if the splice connector was UL listed (it is) and the splice meets NEC standards, this solution meets their installation requirements.
According to the pictures (assume <75% cross section is used), would this still be in NEC compliance?
- The total of all conductors installed at any cross section of the wiring space does not exceed 40 percent of the crosssectional area of that space.
- The total area of all conductors, splices, and taps installed at any cross section of the wiring space does not exceed 75 percent of the cross-sectional area of that space.
- A warning label complying with 110.21(B) is applied to the enclosure that identifies the closest disconnecting means for any feed-through conductors.”