All of the recent posts about fault current made me think of a related question....
How often are you guys asked to provide fault current calculations to the AHJ for commercial work. What about breaker coordination calculations...
I know NEC requires these but I have never been asked to produce them. I do them to insure the system is designed correctly and stick them in a file incase there is ever an issue.
Has anybody found a good way to get fault current calc done before its too late. For example, I can't get POCO xfmr size / impedance or available Issc until I can give them the full load of the building. I don't know full load until design is done. Sometimes I have to go back and change fault current ratings or OCPD types by addendum. anybody got a better way.
How often are you guys asked to provide fault current calculations to the AHJ for commercial work. What about breaker coordination calculations...
I know NEC requires these but I have never been asked to produce them. I do them to insure the system is designed correctly and stick them in a file incase there is ever an issue.
Has anybody found a good way to get fault current calc done before its too late. For example, I can't get POCO xfmr size / impedance or available Issc until I can give them the full load of the building. I don't know full load until design is done. Sometimes I have to go back and change fault current ratings or OCPD types by addendum. anybody got a better way.