Scenario: Electric Vehicle charger installed outside, about 25 ft from its source (a building) next to a parking stall.
The charger is fed with a 40 amp branch circuit, 240 volt single phase. These devices are about 1 ft square, 4 ft tall, with about a 15 ft supply cord for the EV charging
Does this charger require a disconnect (and grounding electrodes)?
Consider:
It meets the Art 100 definition of a structure
225.31 and 32 require a disconnect )disconnect then requires a grounding system per 250.30
225.32 gives us exception 3 for lighting poles, that the disconnect can be located elsewhere.
Soon thousands of these chargers will be installed by cities and businesses.
Being installed by parking stalls they become a bumper magnet and if damaged, how do we access the disconnecting means? How do we turn off the power if the charging cord is cut and stolen?