does the code require the removal of abandon unused wiring
Also you cannot leave dead ended conductors in underfloor raceways like walkerduct etc.
How so?The reason why abandoned cables must be removed is because they are a fire hazard.
The reason why abandoned cables must be removed is because they are a fire hazard.
Really? If it's abandoned, it's no longer hooked up. Is the brand new coil of Romex sitting on the floor of a job site a fire hazard?
The reason why abandoned cables must be removed is because they are a fire hazard.
Sure. The insulation is considered part of the fuel load from a fire safety perspective.
Also you cannot leave dead ended conductors in underfloor raceways like walkerduct etc.
So you can't leave future wires? whats the harm and reasoning in this proposal?
ARTICLE 390
Underfloor Raceways
390.1 Scope. This article covers the use and installation
requirements for underfloor raceways.
390.2 Definition.
Underfloor Raceway. A raceway and associated components
designed and intended for installation beneath or
flush with the surface of a floor for the installation of cables
and electrical conductors.
390.8 Discontinued Outlets. When an outlet is abandoned,
discontinued, or removed, the sections of circuit conductors
supplying the outlet shall be removed from the raceway. No
splices or reinsulated conductors, such as would be the case
with abandoned outlets on loop wiring, shall be allowed in
raceways.
Sure. The insulation is considered part of the fuel load from a fire safety perspective.
I don't see that... and were just talking underfloor raceways here...
Yes, it is part of the fire load, but compared to the finishes and furnishings of the building it is, in most buildings, such a small part of the total fire load it doesn't make any real difference.Sure. The insulation is considered part of the fuel load from a fire safety perspective.
IMO, wires installed for future use are not abandoned conductors, they have never been in use and would not meet the definition of abandoned. They are puposely installed and left for a reason.So you can't leave future wires? whats the harm and reasoning in this proposal?
IMO, wires installed for future use are not abandoned conductors, they have never been in use and would not meet the definition of abandoned. They are puposely installed and left for a reason.
Roger
The OP didn't say anything about raceways.
Also you cannot leave dead ended conductors in underfloor raceways like walkerduct etc.
You may not be familiar with 'walker duct' (AKA Underfloor raceways)
Now if you are making changes to an existing set up and you remove a j-box they don't want you to just stuff the dead ended conductors into the raceway. Think about removing a 4" square from the end of an EMT run, would you pull the conductors back to the next box or would you just stuff them into the EMT and leave them there?