Good afternoon,
One of our project managers who has a design with 56a of inverter output asked me if he can use #4 with a 60a disconnect (Siemens LNF222RA), and a 70a backfeed breaker. I told him no but can't actually find the code that disallows it. 690.8(B) requires conductor upsizing. 690.9(A) requires OCPD upsizing. Where is equipment upsizing required? The best thing I could tell him was the blades on the disconnect are technically conductors and thus would fall under 690.8(B) but I have little confidence in that answer.
Regards,
Barklie Estes
One of our project managers who has a design with 56a of inverter output asked me if he can use #4 with a 60a disconnect (Siemens LNF222RA), and a 70a backfeed breaker. I told him no but can't actually find the code that disallows it. 690.8(B) requires conductor upsizing. 690.9(A) requires OCPD upsizing. Where is equipment upsizing required? The best thing I could tell him was the blades on the disconnect are technically conductors and thus would fall under 690.8(B) but I have little confidence in that answer.