For example if I have a boiler with a zone controller for multi. 120V-1/2 HP circ. pumps. Does the electrical contractor provide this 120V wiring from the zone controller to the pumps or does the HVAC contractor?

I would think the electrical contractor does and the HVAC contractor provides only class 2 wiring.
 

kwired

Electron manager
Location
NE Nebraska
Some places the HVAC contractor may not be allowed to do electrical at all, some maybe not allowed to do electrical over 50 volts, unless they obtain an electrical license also. Some places may have special installers license that limits them to only wiring of their HVAC equipment and they may not even be allowed to install the branch circuit conductors ahead of local disconnect, but can wire most anything else associated with the HVAC equipment.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Here, in Virginia, technically you need to be a master electrician and pull permits anytime wire is run. In the real world, permits are seldom pulled, and when they are, the electrician would be responsible for everything up to the unit itself. Have roughed in many houses where we run the wire to the disconnect, then come back later after the outdoor unit has been set and pull a liquid tight whip to it. Unless the Zone controller has some sort of a factory plug in cord to the pumps, it would be, or should be on the electrician to install that wiring.

HVAC guys can do electrical here because many of them have a licensed electrician working for the company. The chances though of a licensed electrician actually hooking up any Class 2 wiring or anything on the load side of the disconnect is probably close to zero.

The bad part about HVAC guys doing work like that is the many of them will just use the existing wiring and pay no attention to requirements for, say, a fused disconnect, or read the sticker for MOPD. They can make the connections well enough, but there is a lot more to doing it than just that... indicated by the number of oversized Breakers I have pulled out of panels serving HVAC units, especially ones that has been replaced with a newer unit and frequently have the need for the larger breaker of the old one
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I would insist on doing it. It does fall under our responsibility if inspected.

-Hal

In my state of Georgia, a mechanical contractor’s license allows them to install all wiring related to hvac equipment.


Responsibility should be spelled out in the plans & specs if there are any.


Sent from my iPhone using Tapatalk
 