All,
Bought a Fluke T+pro. Thought I might replace my Wiggy with something that does continuity also and has digital readout. The question: Is the impedance of the T+ low enough to rule out phantom voltage measurements. The instructions say ~5mA test current. At 120V, this would be 24 kOhms. It seems like this would be low enough. My DMMs are all in the MegaOhm range.
Thanks,
Mark
Bought a Fluke T+pro. Thought I might replace my Wiggy with something that does continuity also and has digital readout. The question: Is the impedance of the T+ low enough to rule out phantom voltage measurements. The instructions say ~5mA test current. At 120V, this would be 24 kOhms. It seems like this would be low enough. My DMMs are all in the MegaOhm range.