Please advise if NEC 310.15(B)(6) applies to 120v/208v or just 120v/240v.
For one-family dwellings and the individual dwelling units of
two-family and multifamily dwellings, single-phase feeder
conductors consisting of 2 ungrounded conductors and the
neutral conductor from a 208Y/120 volt system shall be permitted
to be sized in accordance with 310.15(B)(7)(1) through
(3).
Please advise if NEC 310.15(B)(6) applies to 120v/208v or just 120v/240v.
Limited in that there will be a 208/120 three phase supply transformer involved - and it very likely supplies other customers. Will also be 200 amp or less in nearly all cases.Our local POCO lists 208Y/120 volt, 1ph, 3-Wire Service as a secondary power option. It is marked as "limited availability".
So set a three phase meter socket and come off load side to a single phase panel.The last commercial job we did that had a 3ph 120/208v service to it, but, the Power Co. would not allow us to even set a 1ph temporary off of their 3ph service.
All of our Temps were made up for 120/240v 1ph,yet they would not simply feed our temporary with 1ph 120/208v off of their existing pots at the top of the pole.
We had to build a 3ph. temporary with a 3ph meter before they would connect to it.
They didn't care what we did with it on the load side of the meter.
JAP>
So set a three phase meter socket and come off load side to a single phase panel.