Matt Mckenzie
- United States
Does non linear mean multiply by 125%? Fluorescent is non linear? Means multiply by 125%?
In general, non-linear loads only affect whether a neutral conductor is counted as a current-carrying conductor for derating purposes.Does non linear mean multiply by 125%? Fluorescent is non linear? Means multiply by 125%?
Amount of extra capacity for non linear loads depends on details of the non linear load(s). Also at the branch circuit level it may be high but at same installation it may be low at the feeder or service level of distribution if there is a lot of linear load on other circuits.The 125% factor is due to it being a continuous load. I.e. operates at its full ampacity continuously for 3 hours or more.
You might think that another 125% factor might apply, because when you count the neutral of a 3-phase circuit as a "current-carrying conductor", that your ampacity adjustment becomes 0.8. The reciprocal of 125%. This is only true for instances when the neutral affects the ampacity adjustment factor.
I'm not familiar with nonlinear loads, so I'm not sure if other correction factors apply. If there are multiples of the 3rd harmonic, these currents add up instead of cancel, when applied to the neutral conductor. This is why the neutral might be larger than the phase wiring.