Does plugging portable UPS into GFCI outlet defeat the GFI protection?

Status
Not open for further replies.

RossS

Member
Location
Research Triangle, NC USA
Occupation
Electrical engineer
We now have two different restaurant clients who want their kitchen data systems (POS, order screens, etc.) to plug into small consumer UPS systems. These in turn, plug in to an outlet in the kitchen, which is required to be GFCI protected. If a ground fault occurs in that equipment causing the GFCI breaker to trip, the UPS will restore the power to the fault, correct? Or do even small UPS systems have a means to detect the fault and not restore the power?
 
Unless the UPS incorporates its own GFCI as part of its output or you add a downstream GFCI, the UPS will continue to power the fault until the fault current becomes high enough to trip a breaker.
In addition, if the output of the UPS is isolated from the input, a fault from the output to ground would not necessarily trip the upstream GFCI in the first place.