Hello all, long-time lurker here but first time posting. I need to settle argument between several of my guys, lol!
Scenario is EMT conduit with wire-type EGC run to self-grounding receptacles in 4" square boxes. 250.148 (C) requires connection between 1 or more EGC's and a metal box by means of grounding screw, equipment listed for grounding, or listed grounding device. The question is can the wire-type EGC be terminated only on the self-grounding receptacle and count the receptacle as the listed grounding device to make the connection to the metal box required by 250.148 (C)?
If yes, then would 250.148 (B) apply? The wire type EGC's are connected together with pigtail to device so in case of device being removed the box is still bonded through the EMT but the EMT would no longer be connected to wire-type EGC. I'm thinking if the device is removed the pigtail could just be taken to the box but we're having to rely on future device removing person to know that.
*Note - here in PA we're on 2017 NEC
Thanks and happy electrician-ing!
Scenario is EMT conduit with wire-type EGC run to self-grounding receptacles in 4" square boxes. 250.148 (C) requires connection between 1 or more EGC's and a metal box by means of grounding screw, equipment listed for grounding, or listed grounding device. The question is can the wire-type EGC be terminated only on the self-grounding receptacle and count the receptacle as the listed grounding device to make the connection to the metal box required by 250.148 (C)?
If yes, then would 250.148 (B) apply? The wire type EGC's are connected together with pigtail to device so in case of device being removed the box is still bonded through the EMT but the EMT would no longer be connected to wire-type EGC. I'm thinking if the device is removed the pigtail could just be taken to the box but we're having to rely on future device removing person to know that.
*Note - here in PA we're on 2017 NEC
Thanks and happy electrician-ing!