T Telc Member Oct 12, 2009 #1 Can the telephone NID boxes be grounded to the meter pan the same as CATV is done with with straps on the rigid mast or corner clamp.
Can the telephone NID boxes be grounded to the meter pan the same as CATV is done with with straps on the rigid mast or corner clamp.
raider1 Senior Member Staff member Location Logan, Utah Oct 13, 2009 #2 Welcome to the forum. Depends on what code cycle you are working under. Under the 2008 NEC you must ground the telephone system to the intersystem bonding termination required in 250.94. Take a look at 800.100 for grounding of telephone systems. Chris
Welcome to the forum. Depends on what code cycle you are working under. Under the 2008 NEC you must ground the telephone system to the intersystem bonding termination required in 250.94. Take a look at 800.100 for grounding of telephone systems. Chris
T Telc Member Oct 13, 2009 #3 Have you used these T&B intersystems bonding connectors? http://tnblnx3.tnb.com/emAlbum/albums//us_resource/gm8101R1lr_bb1.pdf I called called a supplier and I couldn't believe they wanted $60 for them. I asked if it was for a package or case and they said the computer said $60 was for 1.
Have you used these T&B intersystems bonding connectors? http://tnblnx3.tnb.com/emAlbum/albums//us_resource/gm8101R1lr_bb1.pdf I called called a supplier and I couldn't believe they wanted $60 for them. I asked if it was for a package or case and they said the computer said $60 was for 1.