Does Telephone have different grounding requirements then CATV?

Status
Not open for further replies.

Telc

Member
Can the telephone NID boxes be grounded to the meter pan the same as CATV is done with with straps on the rigid mast or corner clamp.
 
Welcome to the forum.:)

Depends on what code cycle you are working under.

Under the 2008 NEC you must ground the telephone system to the intersystem bonding termination required in 250.94.

Take a look at 800.100 for grounding of telephone systems.

Chris
 