Secondary of a transformer has X1, X2, X3, X4 with X2 and X3 Connected together and X4 grounded and bonded. This way X1 to X4 will have 240 Volts and X2/X3 to X4 will have 120 Volts. This is common practice for Extruder Controls. It allows you to use a Single pole Breaker for a heater, and single Solid State Relay to control the heater. The transformer ends up pretty balanced because the 120 V is only used for a cabinet light.
Yes, 250.21 covers it. I knew everyone on the forum was pretty sharp and I just wanted to see if anyone else has ever seen this done. It is a great cost saving because you are still breaking all ungrounded conductors and get 240 V from a single pole breaker. That's what economy switching is.