Does the Center Tap Have to be Grounded?

Status
Not open for further replies.

kpepin

Senior Member
Does the NEC say that the center tap of a secondary on a 480 Volt to 120/240 Volt Single Phase Transformer have to be grounded if it's used for both 120 and 240 volt loads?

(has anyone ever heard of economy switching?)
 
Re: Does the Center Tap Have to be Grounded?

See 250.20

Roger
 
Re: Does the Center Tap Have to be Grounded?

Sorry, not for premise wiring but for say inside a control panel.
 
Re: Does the Center Tap Have to be Grounded?

I'm sure you saw 250.21 while you were on that page, right.

[ January 27, 2005, 08:11 PM: Message edited by: russ ]
 
Re: Does the Center Tap Have to be Grounded?

Unless you have a good reason, that is covered by 250.21 - why not earth it & bond it ?
 
Re: Does the Center Tap Have to be Grounded?

Secondary of a transformer has X1, X2, X3, X4 with X2 and X3 Connected together and X4 grounded and bonded. This way X1 to X4 will have 240 Volts and X2/X3 to X4 will have 120 Volts. This is common practice for Extruder Controls. It allows you to use a Single pole Breaker for a heater, and single Solid State Relay to control the heater. The transformer ends up pretty balanced because the 120 V is only used for a cabinet light.

Yes, 250.21 covers it. I knew everyone on the forum was pretty sharp and I just wanted to see if anyone else has ever seen this done. It is a great cost saving because you are still breaking all ungrounded conductors and get 240 V from a single pole breaker. That's what economy switching is.

[ January 28, 2005, 06:01 AM: Message edited by: kpepin ]
 
Re: Does the Center Tap Have to be Grounded?

I think if you look closely all ungrounded conductors will need over current protection.

It is very common to have industrial control panels that use ungrounded 120V power. However, if you do this, you must use ground fault detection of some sort. usually this amounts to a couple of pilot lights.
 
Re: Does the Center Tap Have to be Grounded?

All ungrounded conductors do have OCP, but since one leg is grounded, you still only have 1 ungrounded conductor for 240 volts. You also have 1 ungrounded conductor at 120 V. The 2 legs that are 120 V between them and are not grounded just aren't used together or you would need a 2 pole breaker (or 2 fuses) and that defeats the purpose of "Economy Switching"
 