I present to you an excerpt 695.6(A)(2):
(2) Feeders.
Fire pump supply conductors on the load side of the final disconnecting means and overcurrent device(s) permitted by 695.4(B) or conductors that connect directly to an on-site standby generator shall comply with.........
My question is, by definition how can conductors on the load side of the final disconnecting means and overcurrent device(s) be a Feeder as the heading indicates?
(2) Feeders.
Fire pump supply conductors on the load side of the final disconnecting means and overcurrent device(s) permitted by 695.4(B) or conductors that connect directly to an on-site standby generator shall comply with.........
My question is, by definition how can conductors on the load side of the final disconnecting means and overcurrent device(s) be a Feeder as the heading indicates?