Im working on a ambulatory type facility that is going to fall under category 1. Based on NFPA 99 (6.4.1.1.8.1 The EPS shall be installed in a separate room for
Level 1 installations. EPSS equipment shall be permitted to be installed in this room). My understanding is that any emergency panels and transfer switches need to be in a different room as normal power? Is that correct? Can someone clarify this?
I would like to per NFPA 110 7.2.3* (Level 1 EPSS equipment shall not be installed in the
same room with the normal service equipment, where the service equipment is rated over 150 volts to ground and equal to
or greater than 1000 amperes.)
Does that mean that if the service is less than 1000A , EPSS could be put in same room as normal electrical room?
Thank you
Level 1 installations. EPSS equipment shall be permitted to be installed in this room). My understanding is that any emergency panels and transfer switches need to be in a different room as normal power? Is that correct? Can someone clarify this?
I would like to per NFPA 110 7.2.3* (Level 1 EPSS equipment shall not be installed in the
same room with the normal service equipment, where the service equipment is rated over 150 volts to ground and equal to
or greater than 1000 amperes.)
Does that mean that if the service is less than 1000A , EPSS could be put in same room as normal electrical room?
Thank you