Does the code require a dedicated circuit? Can it be shared with the dish washer?
Valleybuilt said:It's not DIY, I think I am being charged to much. I have looked at 422-8 it talks about the lenght of the cord, but does it have to be on it's on circuit?
Valleybuilt said:Does the code require a dedicated circuit? Can it be shared with the dish washer?
Dennis Alwon said:It would depend on the load of the dw.
Valleybuilt said:Does the code require a dedicated circuit? Can it be shared with the dish washer?
charlie b said:There is some relevant information in 210.23. But I have found that article to be less informative than I could wish. For example, I don't think it covers the case of two appliances that are both fastened in place and that are both plug-and-cord connected. That is, it doesn't seem (to me, anyway) to cover your situation.
I would recommend you check the listing on the g.d., it could state that it requires its own circuit and how large a circuit also. Good luck.Valleybuilt said:Does the code require a dedicated circuit? Can it be shared with the dish washer?
Question 6. Do a dishwasher and a garbage disposal have to be on separate circuits? Can you have any lighting outlets on with these? ? E.F.
Answer 6. Reference 110.3(b) [NEC 2002], Installation and Use. "Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling." Thus, if the manufacturer specifies a separate dedicated circuit for a dishwasher or garbage disposal, then the response is yes.If a separate circuit is not indicated, then we must review Section 210.19(A)(1), General.
"Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity" equal to or greater "than the noncontinuous load plus 125 percent of the continuous load."
I would not consider a dishwasher or garbage disposal to be a continuous load. Next, we need to consider Section 210.23(A) 15- and 20-Ampere Branch Circuits. "A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2)." Subsection (A)(1) states, "The rating of any one cord-and- plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating."
Subsection (A)(2) states, "The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied."
The final answer is that it can be done if proper circuit ampacity is provided for and the system branch circuit is designed as indicated. ? Raymond W. Weber, CMP-2
Cavie said:Since this is the second question I've seen from you today, based on the type of questions you are asking, I think you have a VERY good electrician. Keep him around. Can't tell if he's overecharging you.
JOHNEO99 said:I have done residential for 20 years and some municipalities let you do both on one 20ammp circuit but in the last several villages I have had to do 2-20 amp circuits.
ceb58 said:I also have read both your post and what I am getting from it is one of two things.
#1 For what ever reason you do not have any trust in the electricians' judgment even though you really dont have a clue as what may be needed to complete a professional, code compliant install.
or
#2 You may be a GC that we all run into. You begrudge every nickel you pay some one who is trying to run a business, give his employees a decent wage and make a living for himself. You know every nickel and dime you can beat him down will not come off the cost of the home but straight into your pocket along with what you have already allowed for your profit.
Your options are. Get rid of the electrician find one that you trust. However if you posted the cost of some of the items you think he is overcharging some of us may agree that he is in line and some of those here from farther up north may laugh at the price.
Remember, you get what you pay for. If you want cheep that is probably what you will get. You may save a few hundred dollars now but what about down the road. I guarantee it will cost more later to fix cheep
stickboy1375 said:They make you or do you let them make you? That is the question.:grin:
Let's hope not. :roll:peter d said:I always use that evil #14 to wire the GD and DW.![]()