Installer
- DesMoines, Washington
Does the NEC allow using Burndy reducers for oversized conductors at a feed Circuit Breaker?
We are installing a 60 AMP 3 phase 208 V panel. We sized the conductors at 2 AWG properly but because of the long run (200 feet) we have been asked to use 1 AWG to lower the Voltage Drop.
Unfortunately, the Square D QOB 360 60 A 3 phase circuit breaker feeding the new panel will only accept 8AWG to 2 AWG conductors.
Is it a violation if we use Burndy reducers or similar parts to allow the 1 AWG to be downsized to 1 AWG at the supply brView attachment MIKEHOLT.pngeaker?