I'm having a very similar "conversation" with a California based AHJ,
to the one @charlie b reported in this 2014 thread:
I have a UL508A panelboard that "does some stuff" and "controls some things".
The AHJ is complaining about the listed control and switching functions of the UL508 panel board.
The Inspector's point of view was that,
But there's a wrinkle:
The downstream loads from the UL508A box could be cord and plug connected. But that's messy, and the subcomponents downstream are not super portable.
Instead we don't want to cord and plug connect them, we wish to hard wire them in conduit, for safety purposes, meaning using wiring attached to the floor or ceiling like any other conduit.
Thoughts? Anyone offering consulting services on code interpretation in California want to take on a job?
to the one @charlie b reported in this 2014 thread:
Does the NEC apply?
I recently had a disagreement with an AHJ in California. We ultimately found a mutually acceptable solution. But I would like opinions on the original issue. We are doing the electrical design for a restaurant. The designer of the kitchen equipment selected a table that had many different...
forums.mikeholt.com
I have a UL508A panelboard that "does some stuff" and "controls some things".
The AHJ is complaining about the listed control and switching functions of the UL508 panel board.
The Inspector's point of view was that,
- The internal components of the UL508A panel board fall under his jurisdiction.
- The wires from our UL508A circuit breaker(s) to the remote utilization equipment are NEC feeders.
- The entire setup falls under AHJ control not just at time of construction, but continuously, should downstream loads be added or removed (each would require a separate building permit). That the disconnects within the UL508A panel box must be relabeled per NEC 110.22, under AHJ supervision, every time a downstream subcomponent is altered, removed or added. That a fresh load calculation must be approved by the AHJ for each removal or addition.
- We are supplying conductors to a UL listed appliance,
and the internal switching functions are a UL matter not a AHJ matter. - That the device itself needed to be considered in terms of total load, but not it's subcomponent loads.
- That subcomponent loads are utilization equipment not under the NEC.
But there's a wrinkle:
The downstream loads from the UL508A box could be cord and plug connected. But that's messy, and the subcomponents downstream are not super portable.
Instead we don't want to cord and plug connect them, we wish to hard wire them in conduit, for safety purposes, meaning using wiring attached to the floor or ceiling like any other conduit.
Thoughts? Anyone offering consulting services on code interpretation in California want to take on a job?