Does the NEC require RGS elbows when emerging from grade?

Status
Not open for further replies.

indigo731

Member
NEC 300.5(D) does not appear to require RGS elbows to emerge from grade. It
does seem to require a riser with a max. depth of 24" below grade to a minimum
height of at least 8'. My E-House is on 7' pedestals. What is a good way to enter
switchgear (bottom entry) without violating code?
 
I think most inspectors would consider the 8 ft minimum to be where the conduit is exposed. You should be able to enter your gear with no problem, however, I would caution that you keep 300.5(J) into consideration also.
 
NEC 300.5(J)

NEC 300.5(J)

THANK YOU FOR YOUR PROMPT REPLY. I CERTAINLY WILL KEEP
300.5(J) IN MIND WHEN I ADD IT AS AN INSTALLATION NOTE.
 