Thanks. So my drawing clocks the space at 20 sq ft, so I'm simply off the hook, right?In your case, it depends on the floor area of the foyer and the width of that wall space.
According to 210.52(I): Foyers. Foyers that are not part of a hallway in accordance with 210.52(H) and that have an area that is greater than 5.6 m2 (60 ft2) shall have a receptacle(s) located in each wall space 900 mm (3 ft) or more in width. Doorways, door-side windows that extend to the floor, and similar openings shall not be considered wall space.
And you're off the hook becuase there is no wall 3' or greater.Thanks. So my drawing clocks the space at 20 sq ft, so I'm simply off the hook, right?
Thanks, but just for arguments sake, if it were >60 sq ft, but the >3' walls were lined with built in shelving, would there be a requirement or does shelving and cabinetry cancel it?And you're off the hook becuase there is no wall 3' or greater.
Shelving and cabinets are not a wall.Thanks, but just for arguments sake, if it were >60 sq ft, but the >3' walls were lined with built in shelving, would there be a requirement or does shelving and cabinetry cancel it?
I guess trying to second guess "code think", you could say anyone could later demo out the shelving and cabs and then you have a wall without an outlet.Shelving and cabinets are not a wall.
The NEC isn't about what may or may not happen in the future. It applies to the situation at the time of installation nothing more. Second guessing will drive you crazy.I guess trying to second guess "code think", you could say anyone could later demo out the shelving and cabs and then you have a wall without an outlet.
Correctamundo.Thanks. So my drawing clocks the space at 20 sq ft, so I'm simply off the hook, right?
No, it's my real name, just coincidence. And the Howards were really Horwitzes.BTW, is your username from the Stooges? Trivia: his real name was Louis Feinberg, same as my grandad!
My wife keeps kosher, and those laws have a lot in common with NEC, a lot of 2nd guessing of how people can screw it up! But thankfully with NEC there seems to be a limit...The NEC isn't about what may or may not happen in the future. It applies to the situation at the time of installation nothing more. Second guessing will drive you crazy.![]()
We have an inspector in my area that needs to know this! He will "what if" you to death!The NEC isn't about what may or may not happen in the future. It applies to the situation at the time of installation nothing more. Second guessing will drive you crazy.![]()
Then the code is violated by the remover of the 'cabinet' and so would need to be rectified by them.I guess trying to second guess "code think", you could say anyone could later demo out the shelving and cabs and then you have a wall without an outlet.
2023 NEC TXHow does the code treat this small space with no 'wall' except the masonry dumbwaiter shaft? Am I required to bang a hole there to place an outlet! Obviously, there will be outlets nearby in the living room, bath and kitchen, and I suppose one could be placed inside the closet.
View attachment 2576063
Yep, I've known Larry since we were kids curious with electricity. It's his real name.No, it's my real name, just coincidence.
Nope, I was going floor to ceiling. I actually wanted to put the service panel on that wall above a 12" counter and below cabinets, but that's verboten. Gotta put it on the other side of the kitchen, adding 11' to most of the cables.2023 NEC TX
210. 52 (C) Does that "pantry/cabinets" have a counter top? 12 inches or wider?
210.52 (H) (1) Foyers greater than 60 square feet....about 7.7 x 7.7 = 59.2 sq ft
It does not look bigger than a 7.7 sq ft.
TX+MASTER#4544