It's the main fused service disconnect for a large single family residential project.
Looks like they put the main disc. sw. inside some kind of cabinet. I think the main concern here is 110.26(3) Height of working space, which says 6.5' or height of the equip., whichever is greater. This doesn't look like 6.5' to me.
Section 110.26(A) does have this verbiage "likely to require examination, adjustment, servicing, or maintenance while energized". Not sure if this disc. sw. falls within this requirement.
Here is the photo:
Looks like they put the main disc. sw. inside some kind of cabinet. I think the main concern here is 110.26(3) Height of working space, which says 6.5' or height of the equip., whichever is greater. This doesn't look like 6.5' to me.
Section 110.26(A) does have this verbiage "likely to require examination, adjustment, servicing, or maintenance while energized". Not sure if this disc. sw. falls within this requirement.
Here is the photo:
IMG 2404 — Postimages