Problem is two lighting panels being fed by one run of 4 - 1/ C. # 500 kcmil + EG.
Both panels have 300 amp main breakers . Total panel load amps 214 and 217 amps . BUT Each panel feeds a 112,5 kva xfmr. that feeds a 400 amp panel that feeds 4 - 100 amp , 208 / 120V receptacle panels.
It would seem logical to assume a large diversity factor with these receptacle panel loads. Which means the lighting panel loads are low. I tried to attach a copy of the riser diagram but would not attach.
The main supply ACB is rated 800 amp / 400 amp trip.
5oo kcmil is rated 380 Amps at 75 C.
Your experience with this set up and code requirements much appreciated. I think it meets code ?