hi all.....new to this forum and seeking input from the many experienced posters.
I am looking into a job where a customer has a facility feed by a 600 amp 208/120 service. The incoming feeds hit a mdp with a 600 amp main. The customer has contracted with the power company to remove the existing transformser and replace with a new one to increase the service size from 600 to 1200 amps. The customer plans to add a second 600 amp mdp with a 600 amp main. They would be bringing 4 4inch conduits into the ct can with 4 sets of 350 mcm conductors. Two sets of the 350 would feed the existing mdp and two sets would feed the second and new mdp. Is this ok in your opinion?
Can a main disconnect for the 1200 amp service be omitted because shutting down the service could be accomplished with only two throws? Thanks in advance for any input.
I am looking into a job where a customer has a facility feed by a 600 amp 208/120 service. The incoming feeds hit a mdp with a 600 amp main. The customer has contracted with the power company to remove the existing transformser and replace with a new one to increase the service size from 600 to 1200 amps. The customer plans to add a second 600 amp mdp with a 600 amp main. They would be bringing 4 4inch conduits into the ct can with 4 sets of 350 mcm conductors. Two sets of the 350 would feed the existing mdp and two sets would feed the second and new mdp. Is this ok in your opinion?