So I’m doing something a bit different. Designing a 120/240 400A service, using a Siemens meterpak 200a per position 2 position combo with the main shutoff/overcurrent right there in the meter. Feeding two separate 200a main lug panels, one in a retail space and one in an apartment. Was going to either use 600 or parallel 3/0 copper in 3” imc for the service. Not sure what to use for feeder. Without running a seperate ground I’m stuck between pipe or MC.
Was going to ground with two ground rods tied with #6 and a 1/0 to the building, gas, and water where applicable.