NFPA 79 states that:
"6.2.3 Enclosure Interlocking. When required by 5.3.1.4, each disconnecting means mounted within or adjacent to a controlenclosure that contains live parts operating at 50 volts ac (rms value) or 60 volts dc or more shall be mechanically or electrically
interlocked, or both, with the control enclosure doors so that none of the doors open unless the power is disconnected".
In case inside my panel all "live pars" cannot be touched using the "Jointed Test Finger", can I conclude that my panel does not contain live parts and therefore I shuld not mechanically or electrically interlock all doors? THKS!