Yes that would be against code and common sense.Originally posted by Towzzer:
Is it against the NEC code to seal a lv door bell transformer inside drywall as long as the box it's connected to has a plate to access the 120v splice
In other words the NEC expects that if the transformer stops working you will be able to get to it for replacement.110.26 Spaces About Electrical Equipment.
Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment. Enclosures housing electrical apparatus that are controlled by lock and key shall be considered accessible to qualified persons.
On the oil burner / gas furnace j-box.Originally posted by bensonelectric:
Just out of curiosity, where is the best place in a house to conceal the transformer? Assuming the house has either no basement or has a finished basement.
Watch out, the inspector might accuse you of planning to change it to a non-code compliant closet light!Originally posted by magoo66:
I usually put DB xfmr in a closet, either above the door header or high on a side wall.
That's not entirely true Allen. There are other things to consider. Read this thread for more info. You might want to read those code section carefully and rethink your answer.Originally posted by allenwayne:
It`s ok to do this as long as all wiring within that box is rated for it.Take standard bell wire the insulation is not rated if my old memory serves me well![]()