Door swing and disconnect switch

Status
Not open for further replies.

MFS-PDX-313

Member
Location
Tualatin, Oregon, USA
Occupation
Electrical design engineer, Industrial equipment
Is there any code violation in having the door hinge on the same side of an electrical cabinet as the incoming power disconnect?
(see attached photo. the door hinge is opposite of the handle)
I understand that it may not exactly be the best practice, but oftentimes, what our customers ask for and what is best practice don't exactly align.

DOOR_SWING_AC_DISC.png
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As long as you meet the requirements of 110.26 with the door closed there should be no problem.

(Please update your profile to show your occupation/relation to the electrical industry)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The door need to open a minimum of 90°. As long as the disconnect doesn't limit the opening to less than 90° you're good.
 

MFS-PDX-313

Member
Location
Tualatin, Oregon, USA
Occupation
Electrical design engineer, Industrial equipment
Thanks for the information folks! I had spent about an hour and a half scouring through NFPA 70 and NFPA 79 (thank the stars for pdf copies, am I right?) and wasn't finding anything. This gives me much assurance.
 