Are we allowed to put the 18\2 in the same drilled hold with 14\2? There is such a small space between the door and window and so many 14\2 and 14\3 that it is ridiculous. 2017 code. Have a great day. Thank you.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
725.136(I)(1) Either all of the electric light, power, Class 1, non–power-limited fire alarm and medium-power network-powered broadband communications circuit conductors or all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, non–metallic-sheathed, Type TC, or Type UF cables
 