Is there a restriction on what direction the door swings (in or out )
This is a 600 amp 3 phase 120/208 y service with 4 panels taking up most of the room
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Doors on Electric room

Not for the installation that you have described. In 110.26(C)(2) the requirement for out swinging doors and panic bars applies to large equipment rated 1200 amps or more.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Doors on Electric room

We don't want any architects to know that a door is allowed to swing in. Let's keep this a trade secret! :D
 